Electrical Power Lines Use High Voltage Lines to Minimize Power Loss.

I understand that in order to minimize power loss, the electric company will minimize the current since (P = I^2R) . However, I'm confused once I realize that this suggests voltage is inversely proportional to the current.

Is this always the case: is voltage always inversely proportional to current?
 

RemoteDoc

Full Member
10+ Year Member
Jan 18, 2008
18
0
Status (Visible)
  1. Medical Student
Since when is voltage inversely proportional to current? V=IR or I=V/R Either way they are proportional. Where did you get the first statement. I know they also use Alternating Current, instead of Direct Current to eliminate power loss. This is because the Wire, has SOME resistance, and thus some power is lost to the surroundings. AC lessens the degree to this.
 

milski

1K member
5+ Year Member
Dec 30, 2009
2,641
527
Where the rain grows
Status (Visible)
  1. Pre-Medical
For a constant power (whatever the powerplant produces) they are inversely proportional - P=IU. At that point increasing one and decreasing the other does not really matter - the final result is the same. There will always be some losses during the transportation. If R is the resistance of the powerlines, the loss is I^2R. It's a lot easier and cheaper to decrease I by increasing U than to work on decreasing R - that in general involves different materials and is harder and more expensive.
 

SaintJude

Full Member
Jan 4, 2012
1,479
5
Status (Visible)
  1. Pre-Medical
I was in high hopes that you would answer, milski. Thank you. So the voltage is proportional to the current , unless the power is constant. That actually makes sense.
 
About the Ads

milski

1K member
5+ Year Member
Dec 30, 2009
2,641
527
Where the rain grows
Status (Visible)
  1. Pre-Medical
I was in high hopes that you would answer, milski. Thank you. So the voltage is proportional to the current , unless the power is constant. That actually makes sense.

That's a very strong statement - you'll be much better off if you specify exactly what you are changing or keeping constant. For a fixed resistance, the voltage and current will be proportional. For a constant power, the voltage and the current will be inversely proportional.
 

SaintJude

Full Member
Jan 4, 2012
1,479
5
Status (Visible)
  1. Pre-Medical
Yeah, I actually posted in that thread...oh my goodness. But I think I didn't really understand what was going on. If MedPr sees this, I apologize belatedly for giving a useless answer..

Anyway, what worries me is that in both cases (as in the AAMC6 question & the TBR question from the thread) the question stem did NOT state that power is constant!

The AAMC6 was worded a bit less ambiguously but still it just asked:

"Electrical power for transmission over long distances is "stepped up" to a very high voltage in order to"...."
 

chiddler

Full Member
10+ Year Member
Apr 6, 2010
2,439
4
Status (Visible)
  1. Medical Student
i guess. i spent so much time with this question the first time that i remembered that power is constant and got the question right.

plus it's the best answer, anyway. why would our power lines have high voltage unnecessarily if it just increased heat production?
 
This thread is more than 9 years old.

Your message may be considered spam for the following reasons:

  1. Your new thread title is very short, and likely is unhelpful.
  2. Your reply is very short and likely does not add anything to the thread.
  3. Your reply is very long and likely does not add anything to the thread.
  4. It is very likely that it does not need any further discussion and thus bumping it serves no purpose.
  5. Your message is mostly quotes or spoilers.
  6. Your reply has occurred very quickly after a previous reply and likely does not add anything to the thread.
  7. This thread is locked.